burntcoil

Electrical
Sep 28, 2011
75
A single phase fault in a 480V MCC led to 3-phase flashover. This flashover caused some other equipment to trip on Overvoltage on 480V switchgear feeding the MCC that experienced flashover. Can flashover in MCC cause overvoltage spikes upstream in 480V switchgear?
 
Replies continue below

Recommended for you

A single phase to ground fault may cause the line to ground voltages of the other phases to rise to phase to phase voltage.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Any time you have an arc in AC, there is a capacitive effect that raises the voltage. But it's more likely that what waross said is what your sending equipment captured. By the time the ground fault caused a flashover, the voltage increase would have already been recorded.