chairmounted
Electrical
- May 20, 2009
- 6
I am using IEEE 1584 spreadsheet to calculate the arc flash energy downline from a low voltage circuit breaker. The maximum available fault current is 26kA and the Digitrip is set to 18kA instaneous trip. The cell in the spreadsheet turns orange noting 'out of range'. What range are they talking about? 18kA is well below the 26kA that is max available. Any help would be much appreciated.