I am the Maintenance/Engineering Manager at a bulk chemical logistics terminal in south Louisiana that handles many different hazardous chemicals. In particular, I am having issues with thermal relief on long uninsulated pipelines (over 5000' in length) in Propylene Oxide, Dimethylamine Anhydrous and Methanol services.
Following pipeline transfers of these products to and from our customers, we block-in the lines awaiting the next transfer. In all cases, we use Consolidated 19,000 series (3/4" x 1") hard seated thermal relief valves on the lines that relieve back into the storage tanks/vessels as necessary to prevent pipeline overpressure. In summer, these thermal relief valves may operate every couple of minutes (sometimes more, sometimes less) to relieve the line pressure.
I don't believe this type of valve is designed to operate in this manner or at this frequency as they are basically operating as a pressure control valve. We constantly have issues with the reliefs leaking by thus causing inventory reconciliation issues. At times, a new valve will last a matter of months in these services and must be replaced because they "beat themselves to death".
Are there alternative valve designs or other hardware (expansion tanks?) that I should consider in this application? I am meeting with Consolidated later this week for their recommendations.
Thanks
Following pipeline transfers of these products to and from our customers, we block-in the lines awaiting the next transfer. In all cases, we use Consolidated 19,000 series (3/4" x 1") hard seated thermal relief valves on the lines that relieve back into the storage tanks/vessels as necessary to prevent pipeline overpressure. In summer, these thermal relief valves may operate every couple of minutes (sometimes more, sometimes less) to relieve the line pressure.
I don't believe this type of valve is designed to operate in this manner or at this frequency as they are basically operating as a pressure control valve. We constantly have issues with the reliefs leaking by thus causing inventory reconciliation issues. At times, a new valve will last a matter of months in these services and must be replaced because they "beat themselves to death".
Are there alternative valve designs or other hardware (expansion tanks?) that I should consider in this application? I am meeting with Consolidated later this week for their recommendations.
Thanks