I seem to be having a problem with a recurring Crydom D53TP50D ssr that I'm trying to diagnose. This problem is outside my scope of knowledge, so any advise is appreciated. The application & history is: This is a drying oven where the load of the SSR is a 208V 18KW heater assembly controlled by a CAL 3200 controller. The unit operated fine for approximately 6 months & then had a catastrophic failure of the ssr. Thinking that there may have been insufficient cooling in the control cabinet, we added an additional fan. About a year later, over a weekend (when no one was around), there was a car accident that snapped a power pole & took out the power to the building. When we arrived the following Monday the ssr was burned up again which we assumed was somehow due to the power disruption. The next replacement lasted only a few months then just seemed to stop working - no visible damage/failure. Once again the ssr was replaced & was working fine for a few months. This one now 'seems' to be dying as well. The oven is now unable maintain the set point temperature. The controller appears to be telling the ssr, to activate & the ssr seems to be doing so, but the load side of the relay shows strange reduced voltages. I should also say that the load (heaters) have checked out each time the ssr was replaced & the controller re-tuned using the auto tuning program, line voltage is correct & well balanced. Any guidance on how to next to proceed?