We are a small to midrange chemical manufacturer. We are trying to perform SIL level verification on some interlocks associated with railcar unloading. The block valves have open and closed limit switches that alarm on command disagree (ie when the valve position on the limit switches disagrees with how the valve is commanded to go). A command disagree alarm requires immediate correction before the station can be used again.
We have multiple unloading stations. The valves used in the interlock are fully closed each time the railcar is switched out (at least 2-3 times per month) but we only do a full documented field verified and certified functional test 1/yr during a full plant turnaround. The historian captures each time the limit switches make open or closed and the alarm logs capture any alarms such as command disagree.
In SIL calculations how do we take credit for the increased reliability of the valves since they are much less likely to have an unrevealed failure than a valve without limit switches / command disagree alarms? Is it a form of partial stroke testing or do we account for it in a different factor?
We don’t want to have to fully document monthly trips since that will require a great deal more paper work and scheduling the testing is problematic since they are switched when they go empty not a planned schedule. Is the historian and alarm log sufficient documentation to prove we can take credit for the increased reliability?
We have multiple unloading stations. The valves used in the interlock are fully closed each time the railcar is switched out (at least 2-3 times per month) but we only do a full documented field verified and certified functional test 1/yr during a full plant turnaround. The historian captures each time the limit switches make open or closed and the alarm logs capture any alarms such as command disagree.
In SIL calculations how do we take credit for the increased reliability of the valves since they are much less likely to have an unrevealed failure than a valve without limit switches / command disagree alarms? Is it a form of partial stroke testing or do we account for it in a different factor?
We don’t want to have to fully document monthly trips since that will require a great deal more paper work and scheduling the testing is problematic since they are switched when they go empty not a planned schedule. Is the historian and alarm log sufficient documentation to prove we can take credit for the increased reliability?