Interfacing DL-205 with an analog source

Status
Not open for further replies.

clava

Electrical
Aug 4, 2003
1
I have an F2-08AD-1 analog interface module for the Direct Logic DL-205 PLC. I want to connect a 4-20mA signal to it, the signal is already connected to a Honeywell 6300, series controller, i would like to daisy chain this signal to the PLC module, but all that comes to the existing controller is a 2 wire 4-20mA signal, how would i go about connecting this to the PLC.
 
Replies continue below

Recommended for you

you can wire them in SERIES but you'll have to recalibrate the first system when done.
 
One thing to look out for with Autmation Direct Analog modules they are non-isolated!
 