Monday I needed to drain a produced water gathering system for maintenance. This system is supplied by four gas wells with pump jacks on them. The pump jacks discharge directly into the gas gathering system (so they can overcome any system pressure encountered). Three wells flow together in a 2-inch Performance Pipe (spoolable composite) system that terminates at the fourth well and changes to 4-inch Performance Pipe and flows 1 mile into atmospheric tanks and has an elevation change of +200 ft.
The four wells together flow 600 bbl/day of produced water (17.5 gpm). This very small volume flow rate in a 4-inch very smooth pipe should develop less than 1 psi of pressure drop due to friction. The elevation change should cause the head of the 4-inch to be around 85 psig. Actual pressure at the head of the 4-inch was 420 psig. The volume of the pipeline is just under 100 bbl.
At 9:00 am we started blowing the system down into an empty atmospheric tank through a 2-inch line. This line bucked and rumbled for four hours with steadily decreasing pressure and at 13:00 we had recovered 75 bbl and the pressure was under 20 psig (minimum on the gauge we were using) and flow became very intermittent. At that point we decided to break a flange on the 4-inch and see if we could flow the rest of the water into a prepared catchment. When we got the top half of the bolts removed we had an ear-splitting noise of gas escaping and water shooting 50 ft in the air. This went on intermittently for two more hours.
I calculated blowdown time for the line being gas full at 420 psig and got 46 minutes. Drain time for liquid full was about an hour. Anybody have a theory why the gas/water mixture blew hard for 6 hours?
The purpose of draining the system was to install a gas knockout. We installed it Tuesday morning and put the wells back on (with the gas knockout bypassed waiting for electrical connection). By this afternoon the pressure in the system was back up to 420-430 psig. Late this afternoon we put the gas knockout in service and it is shifting considerable gas to gas sales instead of to the 4-inch. After 15 minutes in service the line pressure dropped to 350 psig. Can't wait to see what it is in the morning.
David
The four wells together flow 600 bbl/day of produced water (17.5 gpm). This very small volume flow rate in a 4-inch very smooth pipe should develop less than 1 psi of pressure drop due to friction. The elevation change should cause the head of the 4-inch to be around 85 psig. Actual pressure at the head of the 4-inch was 420 psig. The volume of the pipeline is just under 100 bbl.
At 9:00 am we started blowing the system down into an empty atmospheric tank through a 2-inch line. This line bucked and rumbled for four hours with steadily decreasing pressure and at 13:00 we had recovered 75 bbl and the pressure was under 20 psig (minimum on the gauge we were using) and flow became very intermittent. At that point we decided to break a flange on the 4-inch and see if we could flow the rest of the water into a prepared catchment. When we got the top half of the bolts removed we had an ear-splitting noise of gas escaping and water shooting 50 ft in the air. This went on intermittently for two more hours.
I calculated blowdown time for the line being gas full at 420 psig and got 46 minutes. Drain time for liquid full was about an hour. Anybody have a theory why the gas/water mixture blew hard for 6 hours?
The purpose of draining the system was to install a gas knockout. We installed it Tuesday morning and put the wells back on (with the gas knockout bypassed waiting for electrical connection). By this afternoon the pressure in the system was back up to 420-430 psig. Late this afternoon we put the gas knockout in service and it is shifting considerable gas to gas sales instead of to the 4-inch. After 15 minutes in service the line pressure dropped to 350 psig. Can't wait to see what it is in the morning.
David