I would be most grateful for the forums comments on the following:
a) Has anyone approached an MV switchgear manufacturer for an opinion on whether an MV busbar will withstand approx the first 6 cycle and ½ cycle peak when a short circuit study indicates that the infeed short circuit current with induction motor fault contribution exceeds the Fault rating of the switchgear by a small margin re: 8 % ?
Example: calc Ik” =28kA for approx 120ms (6cycles,UK 50Hz) and Ik =26kA for 3secs
b) Has anyone had a manufacturer provide a non-certified document on old MV switchgear to cater for this situation : a very short time rating re: 28kA for 0.2 sec (10 cycles) ?
c) Apart from the usual fault reduction methods of :bus section open on 2xinfeeds,fault limiting reactor,I limiter,uprating of busbar support structure etc are there any other alternatives other than total replacement of the MV switchgear?
I’ve assumed for the above that the MV Circuit Breakers can be replaced with a higher fault rating
IEC60909 Definitions for reference:
Ik” = initial symmetrical short-circuit current [For above=Calculated infeed s/c r.m.s value + symm r.m.s current from rotating plant]
Ib = symmetrical short-circuit breaking current
Ip = peak short-circuit current (Making Current 1st ½ cycle peak)
Ik = steady-state short-circuit current (rated short time current [3decs])
a) Has anyone approached an MV switchgear manufacturer for an opinion on whether an MV busbar will withstand approx the first 6 cycle and ½ cycle peak when a short circuit study indicates that the infeed short circuit current with induction motor fault contribution exceeds the Fault rating of the switchgear by a small margin re: 8 % ?
Example: calc Ik” =28kA for approx 120ms (6cycles,UK 50Hz) and Ik =26kA for 3secs
b) Has anyone had a manufacturer provide a non-certified document on old MV switchgear to cater for this situation : a very short time rating re: 28kA for 0.2 sec (10 cycles) ?
c) Apart from the usual fault reduction methods of :bus section open on 2xinfeeds,fault limiting reactor,I limiter,uprating of busbar support structure etc are there any other alternatives other than total replacement of the MV switchgear?
I’ve assumed for the above that the MV Circuit Breakers can be replaced with a higher fault rating
IEC60909 Definitions for reference:
Ik” = initial symmetrical short-circuit current [For above=Calculated infeed s/c r.m.s value + symm r.m.s current from rotating plant]
Ib = symmetrical short-circuit breaking current
Ip = peak short-circuit current (Making Current 1st ½ cycle peak)
Ik = steady-state short-circuit current (rated short time current [3decs])