NickParker
- Sep 1, 2017
- 445
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
I think the Mar 23, 2013 date is when you set up your Eng-tips account.
Yes it can be a disconnector switch, but it shall be backupped from the upstream CB, meaning that in case of short circuit the upstream CB shall let pass an amount of energy below the maximum acceptable for the switch disconnector (without being damaged). Every manufacturer has its own coordination tables where you will find specified the downstream SD, the upstream CB and up to which short circuit current the back up is guaranteed. This of course implies that CB and SD shall be of the same brand, as these tests are laboratory made and every manufacturer performs them with his equipment only.See the picture below, Can the incoming device be a disconnector switch or a circuit breaker?
I am looking for both IEC and NEC codes that permit the use of disconnector switches as incomers.
That's an IEC symbol for a breaker (EN617-7 07-13-05) which is actually *not* a disconnector device; the cross is the power switch designator, a proper disconnector has a "T" head. At 0.4kV usually breakers also have disconnecting function (i.e. disconnection under load) but that's not a rule. Since 'disconnecting' is a property depending on contact gap a breaker can disconnect only if it is designed to do so (also important the breaking capacity if under load).| don't think it is either an IEC or ANSI symbol. Looks more like a horn gap switch symbol, but that would not provide the protection needed.