phamENG
- Feb 6, 2015
- 7,650
Got a call from a developer I work with - their plumber did a minor hack job on an I joist. Long rectangular hole - about 10"x4" 3' from bearing on a 24' span. 16" deep joist. Violates the manufacturer's allowable hole dimensions.
I'm trying to work up a repair, but I'm having a hard time finding good resources on this. The ASCE Journal of Structural Engineering has a good article from 2017 on the subject. Sadly it's copyrighted and I can't share it here. I've run an analysis on the joist using EWP Studio, which runs off of the iStruct software platform for those who are familiar with it. I also ran it in ForteWeb with a roughly equivalent TJI (the actual joists are PJIs, which is an APA standardized, performance rated product).
Using ForteWeb, it gives me an allowable shear capacity at the hole in the joist of 562#, as opposed to the original joist which had a shear capacity of 2000#. When I use the regression formulas provided in the paper mentioned above, I get 1,885#. So if we went with a factor of safety of about 3.35, they'd be in agreement.
Using EWP studio, on the other hand, it says the allowable load at the hole is only 315# as opposed to the original joist which had a shear capacity of 1970#. So, again assuming they're using the same research, they are using a safety factor of roughly 6.
My actual shear at the hole is 430#. So I like what Forte is telling me. The EWP studio, on the other hand, would require reinforcement. Using the literature to predict the capacity of the joist with their reinforcement detail, I get up to 2093#. Using the factors of safety above, that would be 625# and 349#, respectively. I joists are governed by ASTM D5055, which requires a factor of safety of 2.1 compared to the 5% tolerance limit with a 75% confidence level.
In short, I'm lost at this point. While the paper mentions that their control group meets the ASTM requirement, they don't go into applying it to their data set. Perhaps that's because the existing data set for the repairs is too small to get a meaningful result? I'm not sure. Anyone have any good ideas? (By the way - I know I'm overthinking this, but I want to know...)