I have a question(s) concerning applied axial forces to an HSS column connection, given:
HSS 8x8x5/16 with W14 beam framing into it.
axial load is 5k
vert reaction 25k
moment is 50 k-ft
part twelve of the manual page 12-26 says the WT tees should be long enough to use flare welds at the corners of the HSS.
if this detail is used do you still have to check the conc force applied to the HSS at top and bottom flange with spec K1,4 and equation K1-9?
If you used this equation 1-tp/B = 0???? because tp = B
in the manual companion, examples spec K, AISC mentions that it is ok to use shorter WT and fillet weld to the flat of the HSS column - as long as you meet the criteria given by K1-9, correct?
given an HSS with less than tf of 1/2" this can really limit the connection, would this problem then be solved with column cladding shown on 12-28?
which connection method is most commonly used (flare weld to the corners or fillet weld to the flat)?
thanks in advance for any advice.
HSS 8x8x5/16 with W14 beam framing into it.
axial load is 5k
vert reaction 25k
moment is 50 k-ft
part twelve of the manual page 12-26 says the WT tees should be long enough to use flare welds at the corners of the HSS.
if this detail is used do you still have to check the conc force applied to the HSS at top and bottom flange with spec K1,4 and equation K1-9?
If you used this equation 1-tp/B = 0???? because tp = B
in the manual companion, examples spec K, AISC mentions that it is ok to use shorter WT and fillet weld to the flat of the HSS column - as long as you meet the criteria given by K1-9, correct?
given an HSS with less than tf of 1/2" this can really limit the connection, would this problem then be solved with column cladding shown on 12-28?
which connection method is most commonly used (flare weld to the corners or fillet weld to the flat)?
thanks in advance for any advice.