How to convert one pipe sie to another in terms of equivelent length? 2

Status
Not open for further replies.

GasDistEng

Mechanical
May 20, 2002
25
Years ago I used a simple furmula to convert one pipe size to another in terms of equivelent length. I.E. 20ft of 2" SCED40 Steel is equivelent to 7.2 Ft of 3" Sched 40. I realize the I can do this with the K values if f is known. I think the equation came from the "Pipeline rules of thumb". I do not have this book in hand. Any help would be appreciated.

Thanks....

 
Replies continue below

Recommended for you

In turbulent flow the pressure drop is roughly proportional to the diameter ratio raised to the power of 5. So a pipe with a 1" ID would have a pressure drop of (2^5 =) 32 times that of a 2" ID line (everything else being equal).

The equivalent length of a 2" line, if calculated as a 1" line, would therefore be 1/32x its actual length.

In your example, 20 ft of 2" line would be equivalent to about 150 ft of 3" line.

Hope this helps.

Katmar
 
I concur with katmar. this is basically assuming that mass flow and friction factor are held constant.
 
I've solved the AGA single-phase equation for length (it is really messy) and created a table that yeilds slightly different results than Katmar's. The term is dominated by the diameter to the fifth, but there is also a log(3.7*D/epsilon) term. With epsilon as small as it is, this gives a non-trival change. For your example of a 20 ft of Sched 40 2-inch (I.D. 2.067 inches, assume epsilon = 0.0015 ft/ft) gives you 158 ft of Sched 40 3-inch (I.D. 3.068 inches).

The ratio of the two ID's raised to the fifth power times the 20 ft gives you 144 ft. That's a 9% difference which is probably not within the accuracy of the calculation. Katmar's way is a lot easier.

David Simpson, PE
MuleShoe Engineering
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips Fora.
 
Thanks for the information. I think I may have some bigger issues - see my post on sizing vent line and "Y" factor.

Thanks again!
 
One simple way to do such a conversion would be to use the Hydraulic Institute Pipe Friction Manual on water.

As an example, the friction drops in ft/100 ft tabulated in the manual are:


2 in. sch 40 3 in. sch 40 4 in. sch 40
GPM e/D=0.00087 e/D=0.000587 e/D=0.00047

100 17.4 2.39 (7.3) 0.624 (27.9)
200 66.3 8.90 (7.4) 2.27 (29.2)
300 146 19.2 (7.6) 4.89 (29.9)

The conversion factors are parenthesized. So, 20 ft of a 2" pipe would be roughly equivalent to 20*7.5=150 ft of 3" pipe, and to 20*29=580 ft of 4" pipe.
 
25326, I am going to give you a star for that one, because unless I needed something super sophisticated, that is the method I would use. QED