vmirat
Structural
- Apr 4, 2002
- 294
I'm designing a structure to support WWR 4x4-W4xW4 wire grid over a 42'x 85' mechanical yard which has 15' tall solid screen walls on three sides and the building on the fourth side (85-foot dimension). The steel structure to support the wire grid includes moment frames for both directions. I'm trying to determine the wind loading on the moment frames.
Since the wire grid is level with the top of the vertical screen walls, my first thought was that the wire grid would not have a wind component since it's open. However, because it is open, and the fact that wind doesn't really travel perfectly horizontal, I'm inclined to add something for wind drag on the wire grid. ASCE 7 doesn't address this situation, so I'm looking for some recommendations.
My first idea was to assume that the wind vector was at a 10 degree angle from the horizontal and then figure out the projected area of the grid.
As a side note, you're probably wondering why I'm doing moment frames. The existing screen walls are only 10 feet high right now. The wire grid has to be at a 15-foot height to avoid the equipment in the yard, so I'm having to add screen panels to the existing, which means the existing columns of the screen walls are no longer sufficient and I have to get creative to support the additional wind load without replacing all of the existing columns. Plus, this mech yard is chocked full of equipment, so column placement is very limited, and I can't support anything off of the building.
Since the wire grid is level with the top of the vertical screen walls, my first thought was that the wire grid would not have a wind component since it's open. However, because it is open, and the fact that wind doesn't really travel perfectly horizontal, I'm inclined to add something for wind drag on the wire grid. ASCE 7 doesn't address this situation, so I'm looking for some recommendations.
My first idea was to assume that the wind vector was at a 10 degree angle from the horizontal and then figure out the projected area of the grid.
As a side note, you're probably wondering why I'm doing moment frames. The existing screen walls are only 10 feet high right now. The wire grid has to be at a 15-foot height to avoid the equipment in the yard, so I'm having to add screen panels to the existing, which means the existing columns of the screen walls are no longer sufficient and I have to get creative to support the additional wind load without replacing all of the existing columns. Plus, this mech yard is chocked full of equipment, so column placement is very limited, and I can't support anything off of the building.