budhiman
Electrical
- Jan 26, 2016
- 60
I want to understand how to have ground fault detection on a water treatment plant (system is ungrounded). The system is fed by a delta connected secondary utility transformer. I understand the requirement one way to detect is using 59G (measure the voltage). My confusion is:
1. Can this is 59G be used with wye-wye connected PT's by measure the residual voltage (sum of line to neutral voltages) since the respective ground fault bus will have zero line to neutral voltage ? Since all the literature's say wye-broken delta.
2. One of the similar post of un-grounded fault detection mentions to use 67N to trip and 59G to supervise. Why is the67N required when 59G can also trip since there will be imbalance of voltages if ground fault occurs? Is this only required in transmission to limit the tripping in respective zones? In this case since the system is fed by a delta connected secondary utility transformer there will not be any ground fault on the primary.
3. Has anyone seen/worked on a system similar to this fed from delta connected secondary utility transformer feeding MV motors (delta-delta system) and the system requires ground fault detection? What did you do to address this?
4. Is there good article discussing the ungrounded fault detection system?
1. Can this is 59G be used with wye-wye connected PT's by measure the residual voltage (sum of line to neutral voltages) since the respective ground fault bus will have zero line to neutral voltage ? Since all the literature's say wye-broken delta.
2. One of the similar post of un-grounded fault detection mentions to use 67N to trip and 59G to supervise. Why is the67N required when 59G can also trip since there will be imbalance of voltages if ground fault occurs? Is this only required in transmission to limit the tripping in respective zones? In this case since the system is fed by a delta connected secondary utility transformer there will not be any ground fault on the primary.
3. Has anyone seen/worked on a system similar to this fed from delta connected secondary utility transformer feeding MV motors (delta-delta system) and the system requires ground fault detection? What did you do to address this?
4. Is there good article discussing the ungrounded fault detection system?