going on line with micro logix 1000

Status
Not open for further replies.

controls2012

Electrical
Sep 10, 2008
17
In are plant the majority of plc's are on the network,If know the IP address boom your there. we have A hand full that are not on the network and sometimes I get tripped up.

I'm attempting to go online with A micro logix 1000, I was given the cables to get me started. I'm using the USB with A
keyspan adapter which I've used this before.

I'm getting A no response from processor at selected path/node - diagnostic status failed ox4. can anybody guide me through this simple task, I've kicked myself long enough.

I'm not sure but i believe it might be in my driver and or driver configuration
 
Replies continue below

Recommended for you

Have you tried going to RSLinx after connecting your cable and doing an "Auto Configure"? This is usually a quick way to check the DF1 connection.

How about if you go into RSLinx and click on RSWho, do you see the processor?
 
When configuring the DF1 driver with a USB2SERIAL adapter auto config rarely works. Just configure it for the correct com port that the usb2ser takes on and 19.2k 8 n 1 no handshakn. If that does not work try different port speeds and if still having issues then the port could be configured for dh485 in which you would need a 1747-uic to connect.
 