living2learn
Electrical
- Jan 7, 2010
- 142
System: (2) 12kV, 2500MW Generators that parallel to a common bus and connect to the main switchgear and power some large loads. The system is a closed transition with the Utility. During normal operation only one utility is present.
I have attached a diagram of the electrical system.
The Problem: When utility is present all the PT’s in the electrical system read the same voltage - life is great. Even though they are configured differently the relay compensates. Now when utility is disconnected and the generators are online the PT voltage at the generators and generator switchgear read 122.7V while the main switchgear (1500’ away) reads 128.6V. How did the voltage rise?? Clearly not enough capacitance in the system, but the system was unloaded during this measurement. The waveform is slightly distorted at 1-2% Vthd.
thoughts?
I have attached a diagram of the electrical system.
The Problem: When utility is present all the PT’s in the electrical system read the same voltage - life is great. Even though they are configured differently the relay compensates. Now when utility is disconnected and the generators are online the PT voltage at the generators and generator switchgear read 122.7V while the main switchgear (1500’ away) reads 128.6V. How did the voltage rise?? Clearly not enough capacitance in the system, but the system was unloaded during this measurement. The waveform is slightly distorted at 1-2% Vthd.
thoughts?