I think this is a straight forward heat transfer-101 question, but that was a long time ago for me. I have a free cooling heat exchanger on a chilled water system and was thinking of adding a VFD to the chilled water flow entering the heat exchanger. It acts as a primary "chiller" when ambient permits and is connected through closely-spaced Tees to a bridge with a variable flow secondary system on the other side (not shown). Please see my attached sketches. I understand that if the secondary flow exceeds the primary, I will lose temperature, so I don't want this thread to go down that road. My concern here is what happens when the system is primary-strong.
The top sketch is the design condition. A constant volume of 60 deg water enters and is cooled to 46 deg. The other side of the plate goes to a cooling tower which delivers 43 deg water. The cooling tower is constant volume. I know that return water temp back to the tower will vary with each scenario, but let's assume a constant 43 degree and constant tower flow for this discussion.
When I go primary-strong, some of the water leaving the Hot Side will recirculate backwards through the bridge and blend with the water entering the hot side. So in the Option A sketch, I show a hot side inlet of 53 deg. What temperature will I now get leaving the hot side? I'm not looking for an exact number, I just want to know if it would be higher or lower than the 46 degs.
The Option B sketch would throttle Hot Side flow to avoid blending. So in that case, I still have the design 60 degree entering water, but my flow is less. I used half of the flow as an example. Again, what can i expect to happen with my temperature leaving the hot side?
In all cases, the temperature going back to the tower will be different, so I am having trouble with the heat balance. The tower side will remain constant flow and constant 43 degree entering water.
I tried making a heat exchanger selection. But, the software won't allow me to hold a selected unit constant and see how it performs under various conditions. I am only able to make new selections each time and try to compare them.
Again, I'm not looking for calculations of those exact hot side dischange temps, I just want to know how they change relative to the design condition so I can decide whether or not to vary the hot side flow. Which Option will give the lower discharge temperature on the hot side?
Thanks
The top sketch is the design condition. A constant volume of 60 deg water enters and is cooled to 46 deg. The other side of the plate goes to a cooling tower which delivers 43 deg water. The cooling tower is constant volume. I know that return water temp back to the tower will vary with each scenario, but let's assume a constant 43 degree and constant tower flow for this discussion.
When I go primary-strong, some of the water leaving the Hot Side will recirculate backwards through the bridge and blend with the water entering the hot side. So in the Option A sketch, I show a hot side inlet of 53 deg. What temperature will I now get leaving the hot side? I'm not looking for an exact number, I just want to know if it would be higher or lower than the 46 degs.
The Option B sketch would throttle Hot Side flow to avoid blending. So in that case, I still have the design 60 degree entering water, but my flow is less. I used half of the flow as an example. Again, what can i expect to happen with my temperature leaving the hot side?
In all cases, the temperature going back to the tower will be different, so I am having trouble with the heat balance. The tower side will remain constant flow and constant 43 degree entering water.
I tried making a heat exchanger selection. But, the software won't allow me to hold a selected unit constant and see how it performs under various conditions. I am only able to make new selections each time and try to compare them.
Again, I'm not looking for calculations of those exact hot side dischange temps, I just want to know how they change relative to the design condition so I can decide whether or not to vary the hot side flow. Which Option will give the lower discharge temperature on the hot side?