Hi All,
How to calculate the short term horizontal displacement (with adopting cracked section of the concrete) on free standing wall with eccentric footing at bottom, which is subjected to wind pressure alone. This is same as calculating torque of cantilever wall.

Thank you
 
Replies continue below

Recommended for you

The majority of the deflection will be due to wall rigid rotation as the soil bearing pressures develop.

So, you need to determine a pressure/settlement relationship for your soils.

----
just call me Lo.
 
Considering this as cantilever, i have calculated as follows for short-term deflection (cracked). Here, Mservice is not exceeded the cracking moment.

sep-BW_enxtvn.png


sep-wind_ci2net.png



sep-_cant-_bm_dnmfyr.png


B = 1000 mm
D = 120mm

Ig = 1000 x 1203 / 12 = 144x106 mm4

n = Es/Ec = 200000/ 26587 = 7.52
Fr = 0.62 SQRT (32) = 3.56 N/mm2
Yt = 120/2 = 60 mm

Mcr = Fr*Ig/ yt = 3.56 *144x106 / 60 = 8.544 kNm

Ma = 5.775 kNm

Ma/Mcr <1, Hence Ie = Ig



Deflection = w (uniformly distributed) *l4 / 8*E*Ig

w = 1.1 kN/m = 1.1 n/mm
loaded length = 2500 mm
total length = 3350 mm
E = 26587 n/ mm2
Ig = 144 x 106 mm4

Deflection = 1.1 * 2500*2500* 2500*3350 / 8 * 26587 * 144x 106

= 1.88 mm
 