boffintech
Civil/Environmental
- Jul 29, 2005
- 469
Am inspector on this job that has a number of 8'x'8 isolated column footings with 9#5 T&B EW. In the detail the top mat of column footing rebar is at the same elevation as the rebar in the SOG. The weather proved to be too difficult for the monolithic placement so the bottom half of the footings were placed and then the SOG was placed. The slab-on-grade rebar is specified as #4 at 16" EW so the contractor switched to #5 @ 16" EW and didn't place anything extra at the columns.
problems:
1. I say he's short 2#5 EW at each column. Is my math incorrect?
2. He placed the SOG construction joint 1-foot from a column line and placed 2' long x 1" dia. smooth dowels through the CJ. So the top mat of rebar specified for the columns along this grid line is discontinuous at this CJ. He says it's OK because the smooth dowels lap it out???
Now I have not asked the EOR about that yet yet, but is there any way that could be right?
Thanks.
problems:
1. I say he's short 2#5 EW at each column. Is my math incorrect?
2. He placed the SOG construction joint 1-foot from a column line and placed 2' long x 1" dia. smooth dowels through the CJ. So the top mat of rebar specified for the columns along this grid line is discontinuous at this CJ. He says it's OK because the smooth dowels lap it out???
Now I have not asked the EOR about that yet yet, but is there any way that could be right?
Thanks.