Dear all,
Reading from Australian standard, AS2885.1 point 3.4.3(see below), it stating that no need to de-rating flanges(eg, B16.5) under 120C, which means design pressure at 90C of 5110KPA, class 300 flange can be still used. And it saying it is refereed from to B31.3, I couldn't find the exact point in B31.3 saying about this. Dose any of you have knowledge about this? Thanks.
AS2885.1
3.4.3 Strength de-rating
Carbon steel and carbon manganese steel flanges and valves complying with nominated
Standards may be used without derating at design temperatures not exceeding 120°C.
NOTES:
1 Reference ASME B31.3, ASME VIII, and MSS SP44 – At temperatures up to 120°C flange
designs are based on (a constant) ultimate tensile strength resulting in no strength derating
requirement.
2 The temperature limit for flanged valves applies only to the flanges. Assurance should be
sought from the valve manufacturer that the valve body and seals are suitable for the required
service conditions.
3 The adoption of a higher design temperature for flanges requires that the pipeline and the
piping each satisfy the stress limits required by the design standard.
4 This permission does not currently apply to vessels designed in accordance with AS 1210
(e.g. filter vessels). AS 1210 currently requires strict compliance with the temperature
derating requirements of B16.5 flanges – although it does permit the use of MSS SP44
Where the pipeline design temperature is above 65°C the yield strength of the pipe steel
shall be derated. The reduction in yield strength shall be 0.07%/°C by which the design
temperature exceeds 23°C.
NOTE: The use of 65°C as a boundary below which no de-rating needs to be applied covers
common gas pipeline compressor discharge temperatures. This exemption results in a step change
in de-rating above 65°C.
[/b]
Reading from Australian standard, AS2885.1 point 3.4.3(see below), it stating that no need to de-rating flanges(eg, B16.5) under 120C, which means design pressure at 90C of 5110KPA, class 300 flange can be still used. And it saying it is refereed from to B31.3, I couldn't find the exact point in B31.3 saying about this. Dose any of you have knowledge about this? Thanks.
AS2885.1
3.4.3 Strength de-rating
Carbon steel and carbon manganese steel flanges and valves complying with nominated
Standards may be used without derating at design temperatures not exceeding 120°C.
NOTES:
1 Reference ASME B31.3, ASME VIII, and MSS SP44 – At temperatures up to 120°C flange
designs are based on (a constant) ultimate tensile strength resulting in no strength derating
requirement.
2 The temperature limit for flanged valves applies only to the flanges. Assurance should be
sought from the valve manufacturer that the valve body and seals are suitable for the required
service conditions.
3 The adoption of a higher design temperature for flanges requires that the pipeline and the
piping each satisfy the stress limits required by the design standard.
4 This permission does not currently apply to vessels designed in accordance with AS 1210
(e.g. filter vessels). AS 1210 currently requires strict compliance with the temperature
derating requirements of B16.5 flanges – although it does permit the use of MSS SP44
Where the pipeline design temperature is above 65°C the yield strength of the pipe steel
shall be derated. The reduction in yield strength shall be 0.07%/°C by which the design
temperature exceeds 23°C.
NOTE: The use of 65°C as a boundary below which no de-rating needs to be applied covers
common gas pipeline compressor discharge temperatures. This exemption results in a step change
in de-rating above 65°C.