3cio
Mechanical
- Oct 20, 2011
- 36
Good day!
Iam a rookie and having difficulties on determining the location of the fire hydrant and deciding the fire flow for the building area.
I am using nfpa 1 for my reference of the needed fire flow. The scenario is that there are multiple buildings with a separation of 6m on each side for the vehicle road. all the building are dormitory building (as per nfpa 101) with 3 floors, 950sq.m each.Type II (111) construction and as per local code it doesn't require automatic sprinkler.
When computing for fire flow needed I add all the floor area (950*3) and use the table on nfpa 1 to determine the fire flow which is 2500 gpm (I used the full flow and not deducted the 75% max. as per the code because the building is not sprinklered) and equivalent to minimum of 3 hydrant with the max. spacing of 122 meters (also from table of nfpa 1).
does it means that every building i will put 3 hydrant each? or i could do space the hydrant that the 3 hydrant would cover 2 or more building?
because putting up the 3 hydrant each building is not economical.. please find attache file proposal. the max. radius per hydrant is 50m as per the local code.
also make a comment on my computation if it is valid.
**note. Is anyone has an experience using the ISO method when determining such case?
Thanks and more power
Iam a rookie and having difficulties on determining the location of the fire hydrant and deciding the fire flow for the building area.
I am using nfpa 1 for my reference of the needed fire flow. The scenario is that there are multiple buildings with a separation of 6m on each side for the vehicle road. all the building are dormitory building (as per nfpa 101) with 3 floors, 950sq.m each.Type II (111) construction and as per local code it doesn't require automatic sprinkler.
When computing for fire flow needed I add all the floor area (950*3) and use the table on nfpa 1 to determine the fire flow which is 2500 gpm (I used the full flow and not deducted the 75% max. as per the code because the building is not sprinklered) and equivalent to minimum of 3 hydrant with the max. spacing of 122 meters (also from table of nfpa 1).
does it means that every building i will put 3 hydrant each? or i could do space the hydrant that the 3 hydrant would cover 2 or more building?
because putting up the 3 hydrant each building is not economical.. please find attache file proposal. the max. radius per hydrant is 50m as per the local code.
also make a comment on my computation if it is valid.
**note. Is anyone has an experience using the ISO method when determining such case?
Thanks and more power