Fire Alarm Cable support

Status
Not open for further replies.

eatapeach

Military
Jun 20, 2013
78
Does the NFPA 72 provide support distance of J hooks for Fire Alarm cable? NFPA 70 provides a support distance for everything except Fire Alarm cable. The manufacture states not to exceed 5' however most cables in the NFPA 70 require a maximum distance of 4'
 
Replies continue below

Recommended for you

NFPA 70 has the requirements for cable supports. The NEC does not distinguish supports of fire alarm cable vs other systems so j-hooks or whatever supports are used are regulated by NFPA 70 not NFPA 72.

Typical spacing for cable or conduit supports is 10-ft, but not everything. For instance, MC Cable whips are limited to a max of 6-ft (if I'm remembering correctly).
 