OK, Hazardous Engineers:
I'm looking for documentation that says it's OK to pass the capillary tube in a bulb-n-capillary temperature switch when assembling in the field. Of course, the switch itself is in an explosionproof enclosure.
I know it's OK to seal a capillary entering a box, because assembled units have been that way for ages:
JCI A19AUC
UE Version
Markel Version
Those are just a few examples, there are many others. I also got the opinion from my instructor at ISA years ago that it was OK to do so in the field. The capillary is metal and it's sealed at both ends, so it would take two failures for the capillary to allow the enclosure to exchange gases with the surrounding air. Plus, in general, the tiny passage through the capillary would serve as a good cooling path for hot gases resulting from an explosion.
I have a good client who is wanting to reject a field installation in which the capillary was passed through a (listed) conduit seal. The argument is that the seal is not listed for use with capillary tubing. However, I can't find any resource that says that capillaries are not allowed through listed seals.
We've had these inspected and accepted by AHJs around the US for 15+ years. I can't, however, find any written justification for using a conduit seal for something that is not a conductor or cable.
The particular arrangement in question is here:
Capillary thru Conduit Seal Pic
Any opinions out there? Even better, any citations? Even a conduit seal manufacturer's data sheet would be good. Obviously, I'm defending my position -- but the client makes a good point.
Many thanks.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
I'm looking for documentation that says it's OK to pass the capillary tube in a bulb-n-capillary temperature switch when assembling in the field. Of course, the switch itself is in an explosionproof enclosure.
I know it's OK to seal a capillary entering a box, because assembled units have been that way for ages:
JCI A19AUC
UE Version
Markel Version
Those are just a few examples, there are many others. I also got the opinion from my instructor at ISA years ago that it was OK to do so in the field. The capillary is metal and it's sealed at both ends, so it would take two failures for the capillary to allow the enclosure to exchange gases with the surrounding air. Plus, in general, the tiny passage through the capillary would serve as a good cooling path for hot gases resulting from an explosion.
I have a good client who is wanting to reject a field installation in which the capillary was passed through a (listed) conduit seal. The argument is that the seal is not listed for use with capillary tubing. However, I can't find any resource that says that capillaries are not allowed through listed seals.
We've had these inspected and accepted by AHJs around the US for 15+ years. I can't, however, find any written justification for using a conduit seal for something that is not a conductor or cable.
The particular arrangement in question is here:
Capillary thru Conduit Seal Pic
Any opinions out there? Even better, any citations? Even a conduit seal manufacturer's data sheet would be good. Obviously, I'm defending my position -- but the client makes a good point.
Many thanks.
Best to you,
Goober Dave