A friend built a plasma pip cutting machine, pretty impressive device that is over 5 tons and can cut a 26 foot pipe up
to 30 inches in diameter into sections with V cuts ready for welding. I gave him a Torque Systems ferro DC power supply
that had been in storage for 30 years to run the stepper motors. The machine gets quite a bit of use and has been in
operation for over three years (those discussing capacitor storage life should take note of this). I get a call that the
drive modules are indicating over voltage fault. This is not surprising since the supply normally runs about 84VDC and
the drive is rated for 80V with the spec saying the maximum allowable voltage is 85V. I don't know at what voltage the
actual fault triggers at but it must be close. He explained that once in a while he would get an OV fault, but this time
all three drives showed OV for half a day. Shop voltage can go quite high at times. His half brother who just graduated
EE designed the system. Impressive software but the drivers are on the edge. They burn out a driver on average every year.
power supply is split so it could be run at 42V.
Anyway, that's the background. I'm leaving town for a while and thought I would just throw in a buck transformer to reduce
the line voltage and maybe that would drop the DC just a tiny bit. Then I get another phone call saying everything is running
fine again. The new information is that when he was getting the OV fault the DC was at 95V instead of 84. My understanding
of ferro regulators is that the voltage couldn't jump that much, just a couple percent. Also that these are capable of +-40%
input voltage. Find it hard to believe the resonant cap is failing like that.
Second question. If I add another small cap to the resonant cap could I reduce the voltage to 80V by shifting the resonant
frequency? Has anyone tried this? Seems like a more elegant solution than adding a couple 25A bridge rectifiers in series
for a voltage drop.