Envelop ,Reference Loads and Meshing
Baltali
13
I've attached a dining hall project below.
I have defined load combinations and earthquake definitions according to TS500.
I would like to ask you that what is the "reference load" included in earthquake definitions section?
Also did i apply the true envelop for this combinations?
Can u offer me any document about load envelops?
Finally, is the meshing near the big square hole that was formed by beams in 2nd and 3rd floor, correctly formed?
Before you proceed with your model it is necessary to delete bed elements. So far I find in your attached file a lot of errors
Beam elements with small length:
11195 ; 11196 ; 11201 ; 11206 ; 11208
11255 ; 11542 ; 11543 ; 11544 ; 11585
11588 ; 11589 ; 11600 ; 11601 ; 11602
11610 ; 11611 ; 11617 ; 11669 ; 11670
11678 ; 11680 ; 11688 ; 11691 ; 11694
11695 ; 11696 ; 11700 ; 11702 ; 11703
11708 ; 11713 ; 11897 ; 11898 ; 13458
13459 ; 13461 ; 13478 ; 13511 ; 13517
13521 ; 13537 ; 13542 ; 13743 ; 13802
13803 ; 13804 ; 13830 ; 13848 ; 13859
13860 ; 13876 ; 13878 ; 13880 ; 15382
15393 ; 15558
Beam elements across more than two nodes:
8961 ; 11192 ; 13877 ; 13879 ; 11633
13937 ; 13939 ; 13940 ; 11193
Missing a lot of beam elements (depending on your design):
1-th floor:
Between nodes 711 and 713
462 and 464
6 and 225
19 and 247
32 and 170
327 and 326
569 and 577
For 2-nd and 3-td floor even more gaps in beams.
Two plate elements on the same location:
13325 = 13345
15257 = 15277
More then two plate elements in the same area:
15311 TO 15320
11743 TO 11752
15321 TO 15329
15331
11753 TO 11762
15342 TO 15351
11774 TO 11783
15332 TO 15341
11763 TO 11772
Bad shaped plate elements:
15135 ; 15152 ; 15178 ; 13203 ; 13220
13246