I am looking into limiting the inrush current as much as possible.
The 150 MVA transformer is 33/150 kV and is to be energized from the 33kV side. The transformer is energized for testing purposes only and will never be loaded.
It is being energized from a relatively week grid, through a small(10MVA) 50/33 kV transformer.
I have looked into solutions such as sequential phase switching to hit the optimal point in the voltage curve resulting in reduced inrush.
But I am very interested in a solution of serial connection of resistors, around 100 ohm. This should effectively reduce inrush current. The resistors can remain in series connection as the transformer should never be loaded (only no load losses of transformer). Can anyone see a fundamental error in this setup or advise if components such as 33kV (3-10kW) are readily available?
any hints/tips greatly apreciated.
The 150 MVA transformer is 33/150 kV and is to be energized from the 33kV side. The transformer is energized for testing purposes only and will never be loaded.
It is being energized from a relatively week grid, through a small(10MVA) 50/33 kV transformer.
I have looked into solutions such as sequential phase switching to hit the optimal point in the voltage curve resulting in reduced inrush.
But I am very interested in a solution of serial connection of resistors, around 100 ohm. This should effectively reduce inrush current. The resistors can remain in series connection as the transformer should never be loaded (only no load losses of transformer). Can anyone see a fundamental error in this setup or advise if components such as 33kV (3-10kW) are readily available?