Earthing test of distribution system.

Status
Not open for further replies.

SauravWest

Electrical
Dec 4, 2019
35
Dear Sirs,

1. How to check the earthing resistance values for 33 kV, 11 kV and LT lines distribution poles?

Regards,
 
Replies continue below

Recommended for you

In a 11 KV O/H distribution line about 1.7 KM (only) and each individual poles are earthed with Earth spikes ( Earth resistance of each location is less than 5 Ohm).

But Inspector is insisting us to provide continious earthing for the said O/H line as per IE rules. I could not traced the same from IE rule book.

Regards,
 