- Dec 9, 2003
- 58
Hi all,
We have some CDG26 Earth Fault relays ( tap range 0.1 to 0.4A, DMT 3 sec) on our system and one of them has failed to trip on a feeder, as a result an upstream transformer has tripped.
We investigated the relay and found out that the relay performs quite satisfactory if tested with conventional injection units.
It is a high burden relay and was tested up to 10 times tap setting with correct operation.
The fault level that had been experienced was more than 10 times, probably around 20 times the tap setting. At that point the relay had maloperation.
We tried to simulate the situation by testing relay @ 20 times tap setting and using a variac and two back to back CTs (ratios: 10/500 and 500/2) in the circuit instead of an electronic test unit. This time the voltage developed across the relay coil was around 100Volts and the disc did not move at all.
Now can I conclude that in the real fault situation, the fault has generated a large voltage across the coil and had shorted the tap contacts and prevented the relay from operation?
If the fault level goes above 10 times tap setting, these relays will not be reliable for the application, as their accuracy of tripping is only up to 10 times. Should we consider phasing them out and replacing them with low burden earth fault relays?
Any ideas? Thanks
We have some CDG26 Earth Fault relays ( tap range 0.1 to 0.4A, DMT 3 sec) on our system and one of them has failed to trip on a feeder, as a result an upstream transformer has tripped.
We investigated the relay and found out that the relay performs quite satisfactory if tested with conventional injection units.
It is a high burden relay and was tested up to 10 times tap setting with correct operation.
The fault level that had been experienced was more than 10 times, probably around 20 times the tap setting. At that point the relay had maloperation.
We tried to simulate the situation by testing relay @ 20 times tap setting and using a variac and two back to back CTs (ratios: 10/500 and 500/2) in the circuit instead of an electronic test unit. This time the voltage developed across the relay coil was around 100Volts and the disc did not move at all.
Now can I conclude that in the real fault situation, the fault has generated a large voltage across the coil and had shorted the tap contacts and prevented the relay from operation?
If the fault level goes above 10 times tap setting, these relays will not be reliable for the application, as their accuracy of tripping is only up to 10 times. Should we consider phasing them out and replacing them with low burden earth fault relays?
Any ideas? Thanks