We have a three phase overcurrent plus earth fault relay installed on a bus tie breaker in which the earth fault element is fed from the residual connection of the three phase circuits. The CTs are IEC P class 1200/1 A. Recently, when the circuit was passing 700 A, the relay tripped on earth fault. The pick up current of 60 A was exceeded and after 90 seconds the trip occurred.
To the best of our knowledge there was no earth fault current in the primary system. Thus our attention is focused on the secondary side. We believe that the CTs are sufficiently accurate and could not have caused this trip.
My question is, "If the CT secondary wiring has been earthed both at the CTs in the metal clad switchgear as well as at the relay panel which is in a control room 80 metres away, what form of EMC or other mechanism could cause secondary circuit zero phase sequence current to flow?"