Does piping for Deluge systems need to pitched ?
I have 5 deluge sytems protecting an glass wall atrium with open nozzles . NFPA 13 call for all dry systems to be pitched , but I would be in the thought process to apply NFPA 15 Water spray fixed sytems(2007) 6.3.3.1 "all water spray systems pipe and fittings shall be installed so the system can be drained "
So any trapped piping would require a drain . Its not in an area where its supject to freezing either .
thanks in advance !
I have 5 deluge sytems protecting an glass wall atrium with open nozzles . NFPA 13 call for all dry systems to be pitched , but I would be in the thought process to apply NFPA 15 Water spray fixed sytems(2007) 6.3.3.1 "all water spray systems pipe and fittings shall be installed so the system can be drained "