bigbb
Electrical
- Jul 12, 2008
- 14
Control loop for motor with VFD . One cable Start, running indication, + another for 4-20MA speed control. Running indication is Dry contact (Delta V 24VDC input card) taken out of VFD (Toshiba).
When everything ready to go ,channel status LED on the input card is blinking. Checked voltages and found out some AC voltage (30VAC) coming from the VFD. Checked the cable(it is long 5 stores up) megger is OK. When power is down for this MCC everything is fine. Another strange thing, we have almost the same package next to this and do not have any problem. Only difference is different VFD (Danfoss). I think this is a grounding issue, because there is no separate ground for power and instruments at the plant. Have to figure out what to do.
Thanks
BB
When everything ready to go ,channel status LED on the input card is blinking. Checked voltages and found out some AC voltage (30VAC) coming from the VFD. Checked the cable(it is long 5 stores up) megger is OK. When power is down for this MCC everything is fine. Another strange thing, we have almost the same package next to this and do not have any problem. Only difference is different VFD (Danfoss). I think this is a grounding issue, because there is no separate ground for power and instruments at the plant. Have to figure out what to do.
Thanks
BB