MFJewell
Mechanical
- Mar 2, 2017
- 366
I am planning to reroute some atmospheric drains in our plant. The drains are open floor drains and hubs from a chiller deck. The current lines are 4" cast iron with what looks like leaded joints. I am planning to use CPVC for the reroute. Two of our chillers are steam turbine driven. When they are running they drain cooling water to local hubs. When this happens, I get readings of just over 200 F at the local floor drains. At the piping tie in point (transition from cast iron to CPVC, which is about 100 ft from the hot water source)I get readings of 145 F. The temperature gradient of the pipe is about 200 F down to 85 F over ~ 200 feet of pipe. CPVC is suitable for up to 200 F. I believe I am ok with CPVC. Does anyone have experience that would dictate otherwise?