Need to know how others are coming up with their I/O wire#'s when using Rockwell ControlLogix PLC's. We're starting to do more of these systems and need a wire # that is easily searchable in the program and also works for as a wire label (it's hard to print more than 9 characters on most wire tags).

We tried to # wires similar to a PLC-5 (example: I00114 - input-rack-slot-bit) but that didn't work because we started to have duplicate #'s. We had I/O modules in the rack with the ControlLogix PLC and also a DeviceNet rack in another panel. We ended up with two rack 1's, two slot 1's,etc.
 
Replies continue below

Recommended for you

For the Devicenet ones could you use the node number? Or set it to a higher node so numbers don't conflict?


David Baird
mrbaird@hotmail.com

Sr Controls Engineer

EET degree.

Journeyman Electrician.
 
With the standard A-B Micro/SLC addressing in mind, what I do is create an "alias" tag for each I/O module in the rack and I give it a name that closely resembles the old micro/SLC addressing scheme. For example, if I have a 16 point input module in slot 3, the Control Logix database will tag is as "Local:3:I.Data(.0 thru .15). Not very helpful when writing a program or trying to assign a wire label. I will create a new tag (DINT) with the name "I3", click on the alias box, and in the "alias for" box, you enter "Local:3:I.Data". Now to address a point on the module, say slot 3, input 7, instead of typing "Local:3:I.Data.7", you now type "I3.7". You can use "I3.7" as the wire tag and as a reference in your drawings.
 
rdub - thanks for the example. From an electricians perspective, many will have difficulty making the leap from "I3.7" to "Local:3:I.Data.7".
 
I have also used this technique with DeviceNet installations. First assume my DeviceNet module is in slot 1. Using RSNetworx, I assign my node 1 I/O to word 11, node 2 I/O to word 12, etc... Again, I create an "alias" tag in the processor called "I111" and make it an alias for "Local:1:I.Data[11]". Now when programming, all I have to use is "I111.0", "I111.1", etc... As long as the DeviceNet installation isn't too large, this will work fine.
 
I just did a project with ControlLogix and our customer had us use their plant standard. Dogleg had a good point. Try this:

"Local:3:I.Data.7" would have a wire tagged as L:3:I.07


 