Anybody seen anything like this before?
We have a fairly good sized AB ControlLogix (1756) installation using 5 ControlLogix chassis containing L55 and L63 processors using Logix5000 v12. We have a peer-to-peer ControlNet network, Separate ControlNet for Remote I/O, as well as a common Ethernet network for communication to the HMIs. The processors are on v12.31 of firmware.
Our problem is we are having various processors failing or "crashing". A red "OK" LED is the only light on the processor. The processor may crash after a few hours(after reloading) or after a week or more. Sometimes they crash when we are using them (online, exercising I/O), sometimes they crash when the machine is down and nobody is around. We have yet to identify a cause or even a common thread. I found a similar description of symptoms in AB's Knowledge base referring to a processor "I_be_dead" error (at least they aren't without a sense of humor), but apparently that was corrected in v10 (or was it?).
To correct the situation, we remove and reseat the processors in the chassis, then reload the program (we've used up the 1-day battery life, more on order). Most of the time this works, sometime it doesn't. The processor occassionally "crashes" on reloading the program. Sometimes it works on subsequent iterations of downloading, sometimes we end up pulling and reseating all the comm cards or cycling power to the entire chassis. Sometimes we spend 2 hours getting a PLC back up and running.
Here's a short list of what we've tried
1. swapping suspect cards/processors
2. upgrading processor firmware
3. reducing network bandwidth usage
4. reducing processor "bandwidth" usage
5. increasing/decreasing HMI comm time slice
6. upgrading comm card firmware
7. reloading processor firmware (possibly corrupted?)
8. Panel/chassis grounding
9. Chassis installation clearances verified.
10. CP interior temperature vs. CLx specs
Anybody have any experience with this? Any new ideas? I'm considering building a 2-axis robot for each chassis so we can remove and reseat the cards remotely....
-Brad
We have a fairly good sized AB ControlLogix (1756) installation using 5 ControlLogix chassis containing L55 and L63 processors using Logix5000 v12. We have a peer-to-peer ControlNet network, Separate ControlNet for Remote I/O, as well as a common Ethernet network for communication to the HMIs. The processors are on v12.31 of firmware.
Our problem is we are having various processors failing or "crashing". A red "OK" LED is the only light on the processor. The processor may crash after a few hours(after reloading) or after a week or more. Sometimes they crash when we are using them (online, exercising I/O), sometimes they crash when the machine is down and nobody is around. We have yet to identify a cause or even a common thread. I found a similar description of symptoms in AB's Knowledge base referring to a processor "I_be_dead" error (at least they aren't without a sense of humor), but apparently that was corrected in v10 (or was it?).
To correct the situation, we remove and reseat the processors in the chassis, then reload the program (we've used up the 1-day battery life, more on order). Most of the time this works, sometime it doesn't. The processor occassionally "crashes" on reloading the program. Sometimes it works on subsequent iterations of downloading, sometimes we end up pulling and reseating all the comm cards or cycling power to the entire chassis. Sometimes we spend 2 hours getting a PLC back up and running.
Here's a short list of what we've tried
1. swapping suspect cards/processors
2. upgrading processor firmware
3. reducing network bandwidth usage
4. reducing processor "bandwidth" usage
5. increasing/decreasing HMI comm time slice
6. upgrading comm card firmware
7. reloading processor firmware (possibly corrupted?)
8. Panel/chassis grounding
9. Chassis installation clearances verified.
10. CP interior temperature vs. CLx specs
Anybody have any experience with this? Any new ideas? I'm considering building a 2-axis robot for each chassis so we can remove and reseat the cards remotely....
-Brad