KernOily
Petroleum
- Jan 29, 2002
- 711
Looking for opinions here... I'll try to explain this as best I can. I have a pumping system consisting of two identical 150 hp 3600 rpm pumps in parallel that provide water to a variable load. The pumps take common suction from a tank. Sometimes there is no demand throughout the day, sometimes both pumps are required to meet the demand. The service is well kill water and the pumpage is 150° F oilfield produced water.
Sometimes the load is below one of the pumps' rated minimum flow so there is a variable FCV bypass to bypass some of the discharge back to the tank. The system must remain pressure charged at all times so that there is adequate flow when the need arises. This is sort of like a firewater system, in that the system has to stay pressured up all the time in case there is a demand. The system is controlled by a local PLC. I am stuck with making these two big pumps work, else I would recommend one big pump and a smaller jockey pump.
I am in a debate with the owner's engineer as to whether this system is better/more easily controlled using a discharge pressure signal or a flow signal to stage the pumps off and on line. I claim the load is better met, and the controls will be more stable, i.e less stops and starts, controlling the pumps off flow; he claims pressure.
My plan is to set the pumps to come on-line each day at 5 am since there is no demand at night. If there is intially no demand upon startup, i.e. if the discharge FT says zero, then open the bypass valve and flow the minimum bypass rate for 5 minutes. If the discharge rate does not increase in this time, i.e. if there's no load, shut off the pump after the 5 minutes. The bypass valve and the second pump will be controlled off the discharge FT.
I'm thinking he may have a point in that it might be a good idea to stage the second pump on-line on a pressure signal. Opinions? Thanks!
Pete
pjchandl@prou.com
Sometimes the load is below one of the pumps' rated minimum flow so there is a variable FCV bypass to bypass some of the discharge back to the tank. The system must remain pressure charged at all times so that there is adequate flow when the need arises. This is sort of like a firewater system, in that the system has to stay pressured up all the time in case there is a demand. The system is controlled by a local PLC. I am stuck with making these two big pumps work, else I would recommend one big pump and a smaller jockey pump.
I am in a debate with the owner's engineer as to whether this system is better/more easily controlled using a discharge pressure signal or a flow signal to stage the pumps off and on line. I claim the load is better met, and the controls will be more stable, i.e less stops and starts, controlling the pumps off flow; he claims pressure.
My plan is to set the pumps to come on-line each day at 5 am since there is no demand at night. If there is intially no demand upon startup, i.e. if the discharge FT says zero, then open the bypass valve and flow the minimum bypass rate for 5 minutes. If the discharge rate does not increase in this time, i.e. if there's no load, shut off the pump after the 5 minutes. The bypass valve and the second pump will be controlled off the discharge FT.
I'm thinking he may have a point in that it might be a good idea to stage the second pump on-line on a pressure signal. Opinions? Thanks!