1Tarzan1

Structural
Jan 27, 2012
1
According to 2009 IBC Chapter 6, Type I thru Type IV construction is divided by the use of non-combustible vs. combustible materials. The addition of A or B defines if the construction is protected or unprotected which is the fire resistance protection applied to structural members and bearing walls; i.e. firerated gypsum board, spray-on fire protection, etc. etc. (not the same as sprinkled or non-sprinkled). Now the question: If type "B" is considered to be "Unprotected", why does Table 601 require fire resistance ratings (applied protections) to "B" categories?
 
Replies continue below

Recommended for you

B = Unprotected – Unprotected means that all structural members of a building or structure has no additional fire rated
coating or cover. Exposed members are only fire resistant according to their natural ability and characteristics....

steve yarnall

 