Vegemite
Electrical
- Jul 28, 2002
- 28
This induction motor has been running successfully for many years on a 3.3 kV switchboard which has become obsolete. It was re-connected to a new 3.3 kV switchboard and the following observed immediately after completion of a successful bump test. What was different about this bump test is that the motor was run for five seconds to ensure that it reached rated speed.
After the motor was stopped and its supply circuit breaker had been racked out, it tripped on earth fault. The motor was uncoupled from its load so after it was stopped it kept on rotating.
The earth fault protection was supplied by a core balance CT located in the cable box of the starter panel.
The motor specification is as follows:
• UN = 3.3 kV
• PN = 315 kW
• Frequency = 50 Hz
• FLC = 65 A
• Speed = 2973 rpm
• Torque (MN) = 1012 Nm
• Winding = star connected
• Class of Rating = S1.
The motor supply cable specification is:
• 3c. 50 mm², Aluminium conductor
• Heavy duty Copper screens
• XLPE insulation with PVC sheath
• Length = 280 m.
The motor earth fault protection details:
• Relay type = SEL710
• Core balance CT = 50/1 A
• Earth fault element = Neutral overcurrent
• Trip current = 0.1 A secondary (5 A primary)
• Trip delay = 0.1 seconds.
The neutral current was captured by the SEL 710 relay and the attached trace confirms the presence of genuine earth fault current with a magnitude of 5.5 A.
After the motor was stopped and its supply circuit breaker had been racked out, it tripped on earth fault. The motor was uncoupled from its load so after it was stopped it kept on rotating.
The earth fault protection was supplied by a core balance CT located in the cable box of the starter panel.
The motor specification is as follows:
• UN = 3.3 kV
• PN = 315 kW
• Frequency = 50 Hz
• FLC = 65 A
• Speed = 2973 rpm
• Torque (MN) = 1012 Nm
• Winding = star connected
• Class of Rating = S1.
The motor supply cable specification is:
• 3c. 50 mm², Aluminium conductor
• Heavy duty Copper screens
• XLPE insulation with PVC sheath
• Length = 280 m.
The motor earth fault protection details:
• Relay type = SEL710
• Core balance CT = 50/1 A
• Earth fault element = Neutral overcurrent
• Trip current = 0.1 A secondary (5 A primary)
• Trip delay = 0.1 seconds.
The neutral current was captured by the SEL 710 relay and the attached trace confirms the presence of genuine earth fault current with a magnitude of 5.5 A.