PQ101
Electrical
- Oct 30, 2009
- 67
As soon as the newly installed chiller starts-up the reception on AM radio signal disppears for appx. 5-6 blocks. The 200Ton chiller is equipped with harmonic filter. Equipment manufac. has replaced all circuit boards, the SCR panel, installed isolation transformer, chokes around the cables, installed PVC on incoming power conduit, etc. but made no change.
You can basically hear compressor motor whining-distortion on AM radio anywhere from AM500 thru AM1500.
To start with grounding from 480V Main panel to isolation transformer to chiller starter enclosure to compressor motor was checked for proper installation as per NEC and verified OK. Plan was to set power analyzer to check for waveform distortion including the equipment ground.
As soon as chiller is shutoff the AM radio signal comes back to normal. Appreciate any help to narrow down the cause.
You can basically hear compressor motor whining-distortion on AM radio anywhere from AM500 thru AM1500.
To start with grounding from 480V Main panel to isolation transformer to chiller starter enclosure to compressor motor was checked for proper installation as per NEC and verified OK. Plan was to set power analyzer to check for waveform distortion including the equipment ground.
As soon as chiller is shutoff the AM radio signal comes back to normal. Appreciate any help to narrow down the cause.