What is the formula for converting GPM to BTU /BTUhr
 
Replies continue below

Recommended for you

Not sure what your application is, so I will take a guess. The following formula is used in the HVAC industry and is accurate enough for flow requirements in a building heating system using water for heat transfer.


q BTU/hr
deltaT Temperature drop of water in degF
Qw Quantity of water in Gallons per Minute


q=500*Qw*deltaT
 
there is no formula to convert gpm to btu/hr as the two units of measurement are not equivalent. gpm - volumetric flow rate and btu/hr - a rate of energy per hour.

further description or explanation of the problem is needed to provide a succinct response.

-pmover
 
TechSup01
As you can tell from pmover's correct response, it is impossible with the information you gave, and easy with more information.

The BTU/gal factor for water is zero, so multiplying that factor times any volume flow rate yeilds zero BTU/hr. On the other hand, deisel has several thousand BTU/gal and you can get meaningful answers.

David Simpson, PE
MuleShoe Engineering
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips Fora.

The harder I work, the luckier I seem
 
CRG had it right. You can compute rate of heat absorbed or rejected by water by the equation q = 500xgpmxdT where dT is the temperature difference expressed in deg.F.

 

The formula (CRG and quark) is expressly used for water to which one can attach a Cp value of 1 Btu/(lb.oF).
This is the missing factor to get q in Btu/h.
 

The "formula":

q=500*Qw*deltaT

is a misnomer. It is the equation for the transfer of sensible heat via the use of heat capacity, as 25362 has noted.

It is not a conversion "formula" for converting liquid flow rate to energy flow rate. One has exactly nothing to do with the other. There is a major problem in the logic and communication of techsup01's question.

If he wants to convert liquid flowrate into energy flowrate, he needs a miracle, not a formula. If he wants help to find the sensible heat transfer from/to a liquid flowrate, he has to be able to state or express it correctly - otherwise, we don't know what he needs.
 
Wow, for a minute there I thought I missed that class :)
 
You guys are a tough lot.

Random House Webster’s Dictionary defines a formula as, “any fixed or conventional method or approach.” Which is exactly what q=500*Qw*deltaT is in the HVAC world. I have never seen this formula written as a dimensionally homogeneous equation within the HVAC engineering groups I have worked with. I have worked for several consulting engineering firms and the standard convention for HVAC is q=500*GPM*deltaT

There is a lot more missing than what 25362 has noted: Cp of 1 BTU/(lb*degF)
Also missing is the conversion of mass to volume and minutes to hours.

I put my psychic hat on and tried to guess at what techsup01 was looking for. Note that techsup01 never requested a unit conversion for GPM to BTU/hr. He asked for a formula to convert GPM to BTU/hr which is what I posted. I said that I had to guess at what techsup01 wanted. I prefaced the formula describing its use in the HVAC industry. I have never seen the dimensionally homogeneous equation for water heat transfer written out by the HVAC guys as follows:

q=1BTU/(lb*degF)*64.5*lb/ft^3*Qw*gal/min*60*min/hr*0.134*ft^3/gal*deltaT*degF

Where
deltaT is the change in temperature of the fluid in degF
Qw is the flow in gallons per minute
q is the heat tranfer in BTU/hr

Today I did see where techsup01 posted the same question in the HVAC forum. So techsup01, did I guess correctly?
 

CRG, it appears the unit conversions you considered "missing" are included in the factor 500 as follows:

62.38 lb/cf [×] 0.1336 cf/usg [×] 60 min/h = 500 lb/h​
 
David and Art,

thanks for "rising above the occasion" and attempting to clarify the problem or at least attempt to solicit further information from techsup01.

CRG, no, we really are not a tough lot. we are just applying fundamental principles we all learned or practical advise to requests and try to avoid guesswork.

also, techsup01, you should only post your question in one forum, hopefully the forum suited to the matter at hand. thanks for your cooperation.

good luck!
-pmover
 

To be exact in cancelling units I should have written:

62.38 lb/CF [×] 0.1336 CF/USG [×] USG/min [×] 60 min/h = 500 lb/h​
 
Thanks to all for your help and criticism. The formula I was looking for is: GPMx500xDelta T = BTU/hr. I am new to this site and will try to be more clear in my questions.
 
Wow, what a thread. Actual energy flow is BTU/hr. This takes the form of Q = q*h*dT.

q = gpm as a flow rate.
h = enthalpy of the fluid moving the energy, or its capacity to move energy. h is temperature and fluid type dependent and as such there are many tables for determining the h value.
and delta T describes the two end states.

I hope the calculation doesn't need to be accurate like for sizing of components. I presume the 500 is the "nominal" value used by the HVAC industry for simplification.

Bill

Bill Swain
Ultra Electronics Precison Air Systems
Technical Coordination Manager-US Programs
swainw@asme.org
 
That doesn't make sense. Enthalphy has units of BTU/lb (or whatever system of units you want to use). If q is gpm, then you need a conversion factor in there to convert to a mass flow like lb/hr. There's not need for the dT term.

Now, if you replace h (enthalphy) by a heat capacity (BTU per lb per deg F), then you need the dT term.

Enthalphy is simply the energy content of the fluid relative to some basis, I don't understand your statement "enthalpy of the fluid moving the energy, or its capacity to move energy"
 
Sorry,

I was trying to take a comprehensive answer involving enthalpy and put it into what seems to be someone looking for a generic answer of two different fluid flowing terms. What I meant by "ethalpy of the fluid moving the energy, or its capacity to move the energy" was to try to illustrate in words the concept that the fluid has an energy content related to BTU/lbm of moving fluid. Versus, the concept of GPM which is only a volumetric flow rate. The answer given with volumetric flow rate (GPM) * 500 * dT to get to BTU/hr seemed rudimentary as BTU/hr relates to the the amount of BTU/lbm of the liquid and that is temperature dependant.


Regards,
Bill