For power cables that will be utilized on a 480 V, 3 phase, high resistance grounded system; what should be the selected cable insulation level?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
But the insulation is not between phases, it is from one phase conductor to ground (assuming the cable is laid in a grounded raceway). You have two thicknesses of insulation between phases.Based on 173% of phase-to-phase voltage it would not be adequate.
Nor do I.jghrist said:I see no basis for requiring the insulation to be rated for 173% of phase-to-phase voltage.
173% of what? Line-to-ground voltage or line-to-line voltage?It doesn't change my world however, since the regulatory bodies do require 173% at low voltage, which they define as less than 1000 volts.