Anyone know the C values for 1" rubber hose, or 2" and 3" flexible hosing, commonly used on hydrant outlets?

I've been assuming 90 or 100.
 
Replies continue below

Recommended for you

Note the NFPA equation the c bimr gave is not the H-W equation. So the NFPA c does not equal the C in the H-W equation, if that is what you wanted.

Engineering is the practice of the art of science - Steve
 
Sorry, I should have been more clear - I am looking for the Hazen Williams C value.

Anyone have a rough idea, am I pretty close using a c of 100?
 
C=100 for rubber hose is probably a conservative value and hardly think that anyone would second guess you for that.
 
I have seen values of 130 that correspond with manufacturer friction loss tables, a little higher than probably occurs with an older hose.
 