ajk1
Structural
- Apr 22, 2011
- 1,791
Background:
I am checking a continuous 2-span built-up sawn lumber beam of a cottage that was constructed within the last year (I had nothing to do with its design or construction). The beam that I am checking is the main floor perimeter beam supporting the main floor, and the wood stud wall above which in turn supoorts a loft and the roof.
Preliminary checking indicates that this beam is over-spanned. The spacing of the supports (number of supports were reduced), and the size of the beam were both increased by the contractor, from the original system designed cottage, but no engineer sized the new setup.
Although certain simpifying shortcuts could be made when designing such a beam, I cannot take such shortcuts when checking because I may put the owner to needless expense strengthening the beam, where perhaps no strengthening is required if more accurate checking methodology is used.
Given:
The 2 spans are about 7 feet and 11 feet, and 2 of the plies of the 4 ply beam are butted at about the 2 foot locatiion from the centre support in one span, and about 3 foot from the centre support in the other span.
Questions:
1. Does Woodworks software account for the location of the joints?
2. When checking manually, how should the butted plies be dealt with? For example, is there a "development length" over which the ply picks up its share of load from the adjacent plies of the 4 ply beam? Are the nails generally adequate to make that tansfer of load?
3. Are "clear" spans rather than centre-to-centre spans entered into Woodworks?
4. Is there any worked example of design or checking of a built-up continuous wood beam with some of the plies butted within the spans?
I am checking a continuous 2-span built-up sawn lumber beam of a cottage that was constructed within the last year (I had nothing to do with its design or construction). The beam that I am checking is the main floor perimeter beam supporting the main floor, and the wood stud wall above which in turn supoorts a loft and the roof.
Preliminary checking indicates that this beam is over-spanned. The spacing of the supports (number of supports were reduced), and the size of the beam were both increased by the contractor, from the original system designed cottage, but no engineer sized the new setup.
Although certain simpifying shortcuts could be made when designing such a beam, I cannot take such shortcuts when checking because I may put the owner to needless expense strengthening the beam, where perhaps no strengthening is required if more accurate checking methodology is used.
Given:
The 2 spans are about 7 feet and 11 feet, and 2 of the plies of the 4 ply beam are butted at about the 2 foot locatiion from the centre support in one span, and about 3 foot from the centre support in the other span.
Questions:
1. Does Woodworks software account for the location of the joints?
2. When checking manually, how should the butted plies be dealt with? For example, is there a "development length" over which the ply picks up its share of load from the adjacent plies of the 4 ply beam? Are the nails generally adequate to make that tansfer of load?
3. Are "clear" spans rather than centre-to-centre spans entered into Woodworks?
4. Is there any worked example of design or checking of a built-up continuous wood beam with some of the plies butted within the spans?