Dan67
Mechanical
- Dec 15, 2002
- 7
I have recently gotten into boilers. I am a trainee. I help maintain two boilers that are used for heating several academic and dorm buildings at a university. The smaller of the two puts out up to 40 tons of steam per hour. During colder periods we start up the larger boiler, which can put out up to 70 tons of steam per hour. The temp. of the steam leaveing the boilers is around 300 F. at 140 psi. There has been a bit of a debate going on, over the best way to bottom-blow the boilers. There is an A valve and a B valve in series. Ideally we would like to have B valve go bad before A valve. If A valve went bad there would be nothing between it an having hot boiler water all over the place. Some say that valve A would hold up better if it is opened (all the way) first, and then valve B is used to meter the blowdown water. Others say valve B should be opened all the way and valve A should be used to actually release the water. Does anyone have an opinion on this? Thanks!