Basic question about motor

Status
Not open for further replies.

Renoyd

Mechanical
Feb 11, 2007
41
For a 40 hp motor with 1.15 service factor, when the motor starts to pull high amps like 52 amps, what would be the horsepower being consumed? Is it still under 40 hp like 38 hp, or it is already higher than 40 hp like 45 hp?
 
Replies continue below

Recommended for you

What's your FLA?
Your loading is roughly (52/FLA)*40HP
Assuming frequency is namepalte and voltage is balanced and matches nameplate.

=====================================
(2B)+(2B)' ?
 
For a 40 HP motor 52 Amps will be more of an issue at 600 V than at 480 V.
If only one leg is high you may have a voltage unbalance issue. You may have a low voltage or a high voltage issue.
The motor may be working at its service factor loading.
The motor may be overloaded.
The relationship between current and HP is not linear, however, for small changes at or near full load, the relationship is approximately linear.
If the voltage is high to the point of saturation, the relationship becomes non linear quickly.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
what was the voltage that supplied to the motor?
 
HP is a relationship to torque and speed. Current generally follows HP but is not a specific determining factor because it can change with applied voltage and power factor. If you can measure Watts (or kW), that would be a better indicator of the actual shaft HP if you are interested. There are plenty of watt meter options available to do that.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln