Base MVA for Transformer impedance on ETAP 1

Status
Not open for further replies.

mastergate

Electrical
Apr 22, 2011
40
I have a tansformer as follows:
Voltage: 60kV / 10kV
Rated power: 45/60/75 MVA (ONAN/ONAF/ONAF)
Impedance voltage at rated power and rated voltage at 75°C: 10% +/- 7.5% tol.(at 45 MVA)

ETAP does not allow to change base MVA (it is always the biggest rating). Please how to specify on ETAP the correct impedance?

Thank you.
 
Replies continue below

Recommended for you

How relevant is to change he MVA base if the end result is the same for the given MVA choose by the program?
 
I find it extremely curious that ETAP would force the use of highest forced cooled rating as a base. You might want to double-check that. For an ANSI-rated transformer, the impedance is always based on the loweest self-cooled rating. IEC generally uses the highest forced cooled rating.

In any event, you can easily adjust the %Z by changing bases. (%Z at 45 MVA) = (%Z at 75 MVA) x 45/75

Cheers,

Dave
 
mastergate,
Why donot you contact ETAP HELP desk for this type of program related specific questions?
 
@dpc

Z Base: This value is used as the base MVA for the transformer impedance and depends on the standard selection.
ANSI: Base MVA = Class1 MVA.
IEC: Base MVA = the largest available class MVA.
 
dpc is right but take into account that if you have the Z at 45 MVA and need it at 75 MVA the conversion is the other way around, like:

(%Z at 75 MVA) = (%Z at 45 MVA) x 75/45
 