I have some dilemma on ASCE 7-05 Sec 6.2. Definition of Building enclosure classification.
According to ASCE 7-05 Sec 6.2.,
Building OPEN: a building building having each wall atlest 80% open.
Building PARTIALLY ENCLOSED: a building which complies with both
1-total area of opening in the wall receiving positive external pressure exceeds total area of opening in the remaining building envelope by more than 10% ( area of windward opening shall be 10% more than total area of opening in the remaining sides including roof)
2-total area of opening in the wall recieving possitive external pressure exceeds the lesser of 4ft2 or 1% of area of that wall (minimum area of windward opening shall be lesser of 4ft2 or 1% of area of windward wall )
Building ENCLOSED: a builing that does not comply with the requirements of open or partially enclosed building.
Consider a one-story, 10ft tall box-shaped building having 10ftx10ft footprint. no opening in the roof. Assume each side of the building has 70% opening in walls. How would you classify this building? I have a feeling that it should be classified as "PARTIALLY ENCLOSED". But, according to ASCE 7-05 Sec 6.2 it appears to fall in "ENCLOSED" catergory.
I requested a code opinion from ICC staff and I am waiting on their response.What do you folks think?
According to ASCE 7-05 Sec 6.2.,
Building OPEN: a building building having each wall atlest 80% open.
Building PARTIALLY ENCLOSED: a building which complies with both
1-total area of opening in the wall receiving positive external pressure exceeds total area of opening in the remaining building envelope by more than 10% ( area of windward opening shall be 10% more than total area of opening in the remaining sides including roof)
2-total area of opening in the wall recieving possitive external pressure exceeds the lesser of 4ft2 or 1% of area of that wall (minimum area of windward opening shall be lesser of 4ft2 or 1% of area of windward wall )
Building ENCLOSED: a builing that does not comply with the requirements of open or partially enclosed building.
Consider a one-story, 10ft tall box-shaped building having 10ftx10ft footprint. no opening in the roof. Assume each side of the building has 70% opening in walls. How would you classify this building? I have a feeling that it should be classified as "PARTIALLY ENCLOSED". But, according to ASCE 7-05 Sec 6.2 it appears to fall in "ENCLOSED" catergory.
I requested a code opinion from ICC staff and I am waiting on their response.What do you folks think?