Arc flash study 1
StephWri
13
Can someone direct me to a clear explanation of the equations shown in Annex D of NFPA 70E? I have been trying to reconcile some calculations I did recently and am coming up with widely different answers.
That is a pretty broad question, be more specific
To be more specific; I used NFPA 70E equations D.8.2 and D.8.3 to determine the incident energy and also used Table D.8.7 and got very different answers. Unless I really screwed up the math I don't know why the results are different.
One is for fuses, the other is for breakers. The assumptions are different for each method. What clearing time did you use?
The IEEE equations (D.8) are empirically derived from test data. This means, unfortunately, that they have little (known) physical basis. The equations in section D.8.6, D.8.7 were further derived after additional testing, usually on the behest of some manufacturer, so that they could say their products are better because they are current limiting.
Current limiting does work, and that is part of the reason why these equations are different. They assume that the device will operate, usually within a quarter of a cycle, and that the current will never reach the peak value, which is what you have input into the equation. So, to put it simply, there is less current, and less time, so less arc flash.
I don't know if you could reconcile the two sets of equations. They are based on different assumptions, but even more, they are based on different test data. Hopefully, the next round of testing through the NFPA/IEEE partnership will yield a physics based set of equations, and will put many of the current problems to rest.