Eleceng01
Electrical
- Mar 5, 2007
- 174
We received an arc flash study from a contractor & I have been asked to review it. The contractor did not model any of the protective devices (PD), but made these assumptions.
1) That the first PD will operate in 6-cycles.
2) That the backup PD will operate in 1-second if the first fails.
I am ok with the first one since a relay + breaker time can be 6-cycles. But my review shows many of the arc flash values that they provided are at 2 seconds (I assume from IEEE 1584). Our managements issue is that according to the report, everything is >40cal/cm^2.
I know you need to consider 'worse case' at a location, but it seems to me it isn't right.
Is anyone else doing/seeing studies in this fashion?
I believe that you need to model the relays, fuses, etc. - specifically we have a bus differential on our main bus that they claim is >40cal/cm^2 & I have a hard time believing this.
Am I missing something on NFPA 70E?
Thank you in advance for your thoughts on this.
Kevin
1) That the first PD will operate in 6-cycles.
2) That the backup PD will operate in 1-second if the first fails.
I am ok with the first one since a relay + breaker time can be 6-cycles. But my review shows many of the arc flash values that they provided are at 2 seconds (I assume from IEEE 1584). Our managements issue is that according to the report, everything is >40cal/cm^2.
I know you need to consider 'worse case' at a location, but it seems to me it isn't right.
Is anyone else doing/seeing studies in this fashion?
I believe that you need to model the relays, fuses, etc. - specifically we have a bus differential on our main bus that they claim is >40cal/cm^2 & I have a hard time believing this.
Am I missing something on NFPA 70E?
Thank you in advance for your thoughts on this.
Kevin