What would be a practical approach for assessing actual arc flash hazard risk level when one is just walking inside a 230kV switchyard (N. American case)? It does not seem to me that empirical formulas in NFPA 70E and IEEE 1584 would be adequate to use since, given the typical fault level of say 40kA, being well over 10,000MVA, it will result in such HRC level of hundreds of kcal/cm2 for somebody waking just 4-5m below the bus (at his head level), which would make entering the substation prohibitive irrespective of the PPE level. It seems to be that NFPA 70E and IEEE 1584 formulas are accurate enough for panel type of indoor switchgear up to about 25kV, but applying the same rules for a 230kV facility with high SC level seems to suggests that even drive by on a public road passing by the sub can be classified extremely danger… Thank you.