Executive Summary said:1. Root causes of collapse:
1.1 Inadequate Capacity of Wall System
1.2 Inadequate Shoring
2. Proximate causes of collapse:
2.1 Improper Understanding of Original Building Construction
2.2 Inadequate Construction Documents
2.3 Neglect of Composite Wall
2.4 Inadequate Oversight of Repairs
2.5 Inherent Weakness of West Wall
2.6 Inadequate Repair Techniques
2.7 Inadequate Frequency and Type of Maintenance
Select Structural Engineering assumes no liability on construction or demolition means and methods.
The removal of multiple wythes of masonry during the repair work in the three days preceding the collapse severely compromised the western bearing wall and caused it as well as the areas it supported to collapse on May 28, 2023.
The engineers and masonry contractors responsible for repairs to the Building repeatedly misidentified the structural bearing wall as a nonstructural system. As such, they underestimated the significance of the observable signs of distress in the wall, delayed necessary repair work, designed and installed a weaker replacement system, and removed significant portions of the wall without first installing adequate temporary shoring.